[–] [email protected] 3 points 9 months ago

I honestly don’t see a reason why it would hurt if there’s nothing wired to the breaker. And it feels safer than leaving the contacts exposed since the metal cover is open on those slots. But I’m not sure if that’s the proper way.

As for the wire, I think it’s more so quality control. If it’s new and you bought it then you know it’s high quality and if it doesn’t work you can warranty your own work, but you can’t warranty old equipment. But this is another one where I can’t see the harm in using it if I am replacing a short strand of wire and it is the right length. Like I said, it’s type NM cable so it seems to be equivalent to modern romex wire, just a different brand.

 

Hello, I’m back again. A couple small questions this time, nothing major. But I do have a fun story to tell to explain one of the questions. I’ll put all the questions in bulk at the end though for those who don’t care.

For the story, I ran a new circuit for the lights in my basement. I got that project done fine and it works exactly as expected. But on the last step, when I hooked up the breaker I noticed the 15 amp single pole breaker above it had a white wire, not a black. Ok, not the biggest issue. I just need to figure out where it goes and reverse the wires on the circuit because I thought they had the black on the ground bar instead of the neutral. Instead the black wire went to a 20 amp single pole breaker. But it gets worse.

That side of the house has a lot of electrical stuff that doesn’t work. Several outlets, outside lights etc. it really could’ve gone to anything. But what it went to I wasn’t expecting. We have an electric radiator in our bathroom that hasn’t worked since moving in. I never payed attention because even on the really cold days the bathroom stayed warm since the rest of the house is fine with heating. Turns out the radiator, which requires a 220v circuit on a double pole breaker, was wired with a 12/2 romex NM wire and wired to 2 single pole breakers…. So that’s disconnected now.

My question is, since the slots are pulled out of the panel can I leave these breakers in there not wired to anything? What is the proper way to close those up?

Also, I took out some fluorescent lights and moved them from the window to the center of the room. In doing so I have a good bit of extra cable. It’s not Romex, but it is 600v NM cable. It’s the black rubbery coating. Is it worth saving this in case I need wire for a spare project or is there some kind of risk to using the old cable?

[–] [email protected] 2 points 9 months ago (1 children)

That was a 240v circuit. It didn’t have a ground because it was 10/3. I had the money to get the stuff with a ground, but they were sold out and I couldn’t get anything for a few weeks so I went with the no ground but it is still up to code and manufacturer approved.

This does have a ground and black is going to the breaker with white and ground going to the ground bar.

[–] [email protected] 4 points 9 months ago

Ya, there is asbestos in the house. It is wrapped around the HVAC in the basement. We were told to get it removed now because it’s not yet a health hazard so I’m working on getting that done. It’s still in good condition and it’s not dangerous until it starts to flake away. But the insulation is newer from a remodel when the last owner turned it into a duplex. So within the last 10 years I am pretty sure

[–] [email protected] 1 points 9 months ago (3 children)

12/2 is what I bought for the basement lights I’m working on. Everything I read said that was the appropriate wire to use so I never even co sidered #14

[–] [email protected] 4 points 9 months ago

I knew it had glass in it but I wasn’t sure if that’s all it was made of. That and the paper backing just made me want to be cautious. But I do know how to handle insulation from tearing a room off my grandparents house a few years ago.

[–] [email protected] 2 points 9 months ago

This is thankfully not knob and tube. The house is old enough for it though. Going in the attic you can see where the wires used to run

[–] [email protected] 2 points 9 months ago (5 children)

I’ve been through 6 electricians and 3 general contractors. Probably more but I can’t keep those numbers straight. They all show up to give a quote then never actually do the work. I’m tired of it.

That being said, the insulation just feels flammable to me. It’s clearly marked otherwise but the paper backing and stuff just made me want to double check

 

Hello, I’m back with another question. Everything a read is telling me yes I can, but it really does not feel right so I’m gonna ask here for good measure. Can I run electrical wire through fiberglass insulation?

In several rooms upstairs the wire comes out of the center of the ceiling then goes across to the window where a fluorescent tube light is installed. Below all that is a drop ceiling tile with insulation packed on top of it. I want to take the fluorescent light out and put a normal light back in which is easy enough. My concern is running the wiring through the insulation. Everything says running it through insulated walls is fine and the insulation itself says it’s non-combustible. But can someone confirm that I’m reading the right stuff?

There’s a gap between two pieces of insulation that I want to run the wire between. Picture attached. Not sure how old the insulation is if that is important.

[–] [email protected] 2 points 10 months ago

Ya, I know I need to jump the ground when wiring to power cable for the dryer. I was going to do 10/3 since I had the money for it, but lowes and Home Depot were both sold out when I went to pick it up. Whirlpool told me 10/2 would work so I just went with that in the effort of saving time. New dryer is delivered Tuesday so I want the wiring done before then. The 30a double pole breaker was easy though. Probably the least questionable part of this process

[–] [email protected] 3 points 10 months ago (1 children)

Yup, I already have the electrical tape to mark it. Though I was told I could mark it red or black and both are universal markings for hot wire. Is that wrong? It doesn’t matter here because I have red tape but for future reference it would be good to know

[–] [email protected] 4 points 10 months ago (2 children)
 

I posted on here the other day about some suspicious 240v cable and followed the recommendations to replace it. I was already leaning that way but was kind of hoping to be told I was overthinking it. But you all confirmed what I thought. I ran close to 25’ of 10/2 cable from the second story to the basement. Nothing is wired yet because it is late and I don’t want to turn on the main breaker.

My step dad let me borrow a 50’ fishing tape and 10’ endoscope which were really helpful. I did not have to cut any walls!

[–] [email protected] 2 points 10 months ago (1 children)

I just finished running the new wire. I really lucked out. My step dad has a 50’ fishing tape and a 10’ endoscope that I was able to borrow. I got a new 10/2 wire pushed through fine. I called whirlpool for the specifications and they said the dryer needs 30 amps and will work with 10/2 or 10/3 wire. I was gonna go for the 10/3 but both lowes and Home Depot were sold out so I went with the 10/2. Got a 25’ roll and it used most of it. Maybe a foot of slack

24
submitted 10 months ago* (last edited 10 months ago) by [email protected] to c/[email protected]
 

Hello,

I have been doing a lot of work remodeling a house I bought. The house was in really rough shape so I was expecting a good bit of work but the last owners laziness and incompetence has really made things worse.

They had the house split into two apartments and we are converting it back to a single home unit. We knocked out a wall and installed new stairs to connect the top and bottom floors. Next we are converting the upstairs kitchen to a laundry room. We have been using the makeshift room for a few months, but we are getting a new washer and dryer. Our current dryer is a compact electric dryer that runs on a 120v outlet. The new will be a standard electric dryer and need a 240v outlet. There is 240v outlet in the room for a range. I am going to pick up a new breaker from lowes with the proper amperage but wanted to check everything else first and I think I ran into an issue with the wire itself.

There are 3 wires, which matches the outlet so I am assuming it is supposed to be 2 hots and a neutral. However, upon closer inspection there is no insulation on the neutral. I peeled back more of the larger insulation around all 3 wires but the neutral wire is uninsulated like it was a ground. Now, I have encountered this in the house elsewhere. Most of the outlets have grounds cut off, but a 3 way switch didn't have the second hot wire so they used the ground as the second hot. I got that "fixed" (I unhooked everything and made it a single switch/light circuit and eliminated the second switch). But I don't know of any 240v wire combinations that would only be 3 wires and include a ground. The wire is definitely thick enough to be 240v wire and each individual wire has multiple "threads" like a 240 wire would. But it is older wire as well so I am not sure if it is just that old that they didn't insulate neutrals when they did this. Is this wire safe to use?

A second, and more minor question, deals with a separate circuit. The house electric is still split and I pay 2 bills, one for upstairs and 1 for downstairs. The upstairs does have an outdoor AC unit on it as well that was installed after we moved in by an HVAC tech so I am trusting that to be installed right. But the entire box for the "upstairs" has 4 breakers. There is a 50amp, 40amp, and 20amp double pole breakers and a 10amp single pole. The 10amp controls a single light and one of the 240v breakers controls the AC. Another controls the range/future dryer outlet. The The 20amp double pole controls everything else upstairs which is ALL 120v. There are a few lights and all of the outlets. Is that safe? Is there a reason to do that? The upstairs is pretty small if that makes a difference, I have just never seen a double pole breaker used for a 120v circuit even if it is pretty large.

Edit: I made the original post on my PC due to the size but I’m adding some pictures from my phone

Edit 2: I am going to buy and run new wire with the new breaker. I showed a picture to my dad and he said nothing matters because that’s an aluminum ground which means the wire needs replaced due to its age regardless. So even if it’s wired wrong now, I am stripping the wire out and putting a new wire and breaker in so it should be done right

 

I’m not talking about necessarily an actual job, because I do it with hobbies to. But if I get focused on something, I need an outside source to bring me back. Yesterday at the end of my shift I found a bug in some code and it bugged me until this morning to work on it. I got to work right at 8:00 and after fixing it kept working. Next thing I know it’s 5:00 and my boss is messaging me asking if I’m still in and if I need help getting out for the weekend. I didn’t even take a lunch today. I wasn’t even hungry, thirsty, or even needing to use the restroom until I got that message. I just started working and got sucked in and forgot about basic necessities.

Does anyone else get this way?

 

Reverse image search says Russian Leather Beetle but I live in Western Pennsylvania of the USA which it says they aren’t native to. Any ideas?

 

Hello,

I am looking to buy a house with a lot of work that needs done. I am hoping to learn a lot from the experience so when I am living in it I can fix more myself rather than pay someone else to get it done. One of the first projects is going to be adding an internal staircase. The home used to be single family, but was converted a few owners ago to a duplex. When they did this they removed the stairs connecting the top and bottom floors. I plan to add that back in and make it single family again.

For the project itself, my step dad will be there to help install the stairs. But I don't want to fully rely on him, even though he does know what he's doing. We have done multiple, simple, project together before including installing multiple decks. The stairs for those were only 4-5 steps and pre-cut at Lowes though so I don't think there is much to take away.

The plan is to install the stairs where the old staircase used to be as I think that will make the most sense, but if I am wrong about that please explain why so I can consider that when viewing the house this week.

What I would like to know is when I am at the house next is what should I look for, how do I calculate what all I will need, what I will need, and if there are any good sources online for this kind of project.

What should I look for:

I am pretty sure the best place to build the stairs is going to be where they already were, but what should I look for that will tell me there is a problem that will arise?

How do I calculate what all I will need and what I will need:

I know I need wood, screws and brackets. I am sure 2 boxes of screws will probably be enough, and a trip to the hardware store will be easy for that. Same with the brackets. But how do I calculate how much wood I will need? What size boards do I use for each component? Will I need anything else?

Are the any good sources online:

My step dad is really handy with this stuff and I know he isn't going to let it get done wrong, but it's a struggle planning stuff ahead with him. When I ask him what I will need, he gives answers like "it depends" or "a lot" but he doesn't go into specifics. I would like to research a good bit on my own so when we do actually get together to do this he just needs to come over and help build it which is what he is great at.

I tried looking at YouTube and some google searches, but not much luck other than this wikihow (https://www.wikihow.com/Build-Stairs) which seems pretty comprehensive but I would like more than one article for a project this big. As for YT, it was videos on building prefab stairs and adding them to a home, or refinishing a current stairway, neither or which apply. If someone could supply a good website, or even a YouTube channel that I did not see I would greatly appreciate it.